# 5kW R410a Ecodan PUHZ-W50VHA2(-BS) maximum output testing

**URL:** <https://community.openenergymonitor.org/t/5kw-r410a-ecodan-puhz-w50vha2-bs-maximum-output-testing/24874>\
**Category:** Heatpump\
**Tags:** heatpumpmonitor\
**Created:** [25 November 2023 20:17 UTC](https://community.openenergymonitor.org/t/5kw-r410a-ecodan-puhz-w50vha2-bs-maximum-output-testing/24874 "2023-11-25T20:17:29Z")\
**Posts on this page:** 1\
**Showing post:** 13

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [1 December 2023 11:43 UTC](https://community.openenergymonitor.org/t/5kw-r410a-ecodan-puhz-w50vha2-bs-maximum-output-testing/24874/13 "2023-12-01T11:43:45Z")

</div>

2nd cycle a lot better but outside temps rising fast 0.72C average, 2.6C at the end.

- 4.84 kW (4.96 kW databook), only 2.4% lower!

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/5/5/5519ee8f7947851aec09a84add7a58635a5ccc09.png)

---

_[View the full topic](https://community.openenergymonitor.org/t/5kw-r410a-ecodan-puhz-w50vha2-bs-maximum-output-testing/24874)._