I use a 3 phase system (Denmark).
How do I set up a feed showing the total power without changing the 3 individual Power feeds?
I do not get summed the 3 phases, as I want it?
How are your obtaining the âpowerâ values from your emonTx?
Remember that almost all UK houses have only a single phase supply, so all the OEM sketches are for single phase unless the name says differently.
So unless you have downloaded the 3-phase sketch, you will be reading the âpowerâ of phases 2 & 3 with a 120° phase shift, which is definitely not âreal powerâ. Apparent power (VA) will however be correct, assuming that the phase voltages are equal.
I donât know the workings of emonCMS in detail, but what you have looks OK to me. If you want to display total power (as distinct from energy), you need to add a second âlog to feedâ after the second â+ inputâ.
It works fine with measuring the total output from 3 feeds, thank you.
Now, I want similar measure Power to kWh and Wh Acc. for all 3 phases.
I can not figure out how I do it?
Can you help me a little bit on the road with 3-phase sketch
Is it emontx3 I need to upload a new sketch?
I use 1 x emontx3 to measure the 3 phases.
There are only very small fluctuations in voltages from the 3 phases, so I accept the miscalculations I have to get there.
Can you give me a link to where I can find 3PHASE sketch.
You will find the 3-phase sketch on GitHub (Resources > emonTx firmware). The same sketch is used for all versions - you configure it to suit the version (Shield or emonTx, radio version, etc) inside the sketch.
You must follow the calibration procedure in the comments, because there are significant differences from the single-phase sketches.
I cannot help you with that. Hopefully, Paul @pb66 will be able to tell you.
I have a feed that sum effect from 3 phases.
Line 2 + 3 + 4 = Total power
I also want Power to KWh summed,
In the same way, I want Wh Accumulator summed.
how do I do it ?
Iâm puzzled, I may be misunderstanding what you want to do, but I note you have called the Power to kWh feed in step 5 âpower1 kWhâ, but it is actually already getting the summed powers of your three power inputs, so a more proper name would be âpower1 2 3 kWhâ, and it is accumulating a Wh total, but in kWh.
If you want to forward that to Wh Accumulator, you need a âx 1000â after step 5 to convert the accumulated kWh to accumulated Wh for the Wh Accumulator.
Thank MikeSims
I am still quite inexperienced in the use of emonPi and EmonCMS, so there will be many stupid questions from me
I miss a deeper description of how EmonCMS system works found it somewhere?
Have tried to set up feeds as you have described.
Does it look correct?
Good weekend
As Mike points out the values are summed by using the +input
processes, So line 4 log to feed
is the sum of the powers, therefore the Power to kWh
in line 5 is a total kWh derived from the total power and is an ever increasing accumulating total kWh for all 3 powerâs.
I cannot see any reason for the Wh Accumulator
, that is a process is a special tool for processing Wh total values as they arrive from a device so that any reset/rollover of the device doesnât reset the total in emoncms eg if you are using 10w every 10s reporting period and the values received were 3100, 3110, 3120, 10, 20, 30 because of a reset. The Wh accumulator
would continue to increase by the difference between âthisâ and âthe lastâ value rather than record the actual value received, eg 3100, 3110, 3120, 3130, 3140, 3150.
The resets or rollovers will not happen the way you are collecting data.
If you are just wanting to record the kWh total in Watts then keep the âx1000â and replace the Wh accumulator with a simple log to feed
otherwise just remove both line 6 and 7.